I have some 10-3 wire that was purchased before wire was color coded. Can I still use it and if I can use it, should I paint it the proper color (orange)?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Your use of the word 'ground' is misleading. Are you talking about green, green with yellow stripes, gray, white or white stripes?pyrguy said:The are only two color requirements in the NEC. One for ground and one for the high leg of three phase systems. Use it up.
I think Chris was getting out the fact that there is a grounding conductor-- the bare or green wire or the grounded conductor- the white or often referred to as the neutral wire. Obviously there are 3 color requirements other than the fact that a 3 phase system is often color coded on the ungrounded conductors or hot wires.pyrguy said:Split away, Ground is what most call it no matter which it is.Don't forget bare wire.![]()
210.5 Identification for Branch Circuits.(A) Grounded Conductor. The grounded conductor of a branch circuit shall be identified in accordance with 200.6.
(B) Equipment Grounding Conductor. The equipment grounding conductor shall be identified in accordance with 250.119.
© Identification of Ungrounded Conductors. Ungrounded conductors shall be identified in accordance with 210.5©(1), (2), and (3).
(1) Application. Where the premises wiring system has branch circuits supplied from more than one nominal voltage system, each ungrounded conductor of a branch circuit shall be identified by phase or line and system at all termination, connection, and splice points.
(2) Means of Identification. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means.
(3) Posting of Identification Means. The method utilized for conductors originating within each branch-circuit panelboard or similar branch-circuit distribution equipment shall be documented in a manner that is readily available or shall be permanently posted at each branch-circuit panelboard or similar branch-circuit distribution equipment.
You know....with tape ..paint...fingernail polish....etc.ICE said:Could one of you electrical gurus please give us a tutorial on the code as it relates to relabeling conductors?