Combination electrical/Mechanical Room

retire09

Silver Member
Joined
Feb 19, 2010
Messages
365
Location
Alaska
I have a plan with an electrical room with a 1200 amp 480 volt MDP and transformer that exits through a cased opening into a mechanical room with a 500,000 BTU boiler and then out a door into a parts room for a repair garage. The building is non-sprinklered and I was going to require a one hour separation for the whole thing.

I don't like the idea of combining the two rooms but don't know of any code that would disallow it.

Am I missing anything?
 
1014.3 Boiler, incinerator and furnace rooms.

Two exit access doorways are required in boiler, incinerator and furnace rooms where the area is over 500 square feet (46 m2) and any fuel-fired equipment exceeds 400,000 British thermal units (Btu) (422 000 KJ) input capacity. Where two exit access doorways are required, one is permitted to be a fixed ladder or an alternating tread device. Exit access doorways shall be separated by a horizontal distance equal to one-half the maximum horizontal dimension of the room.
 
The combined space is only 300sf and the electrical space has a continuous and unobstructed way of egress travel per 110.26©(2)a.

I thought about requiring the door from the mechanical room to have panic hardware but I felt that you have alredy exited the electrical room/space when you passed through the cased opening into the mechanical side.
 