• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Commercial Kitchen Door Fire Rating

townofgardiner

Registered User
Joined
Sep 7, 2023
Messages
1
Location
Ulster County NY
I'm working with an architect on confirming the rating for a door leading into a commercial kitchen from a dining room. He specified a standard grade 0 hour rated door with standard glass. I didn't approve the specifications and sent notes back after plan review that said the door should have fire rated ceramic glass. He's insistent that the door doesn't need to be fire rated or need to have fire rated glass. It's a commercial building with a dining room and kitchen. He also specified that the walls for the kitchen separating dining from kitchen can be zero hour rated. I'm searching for references in the code to confirm.
 
The kitchen is an A-2 under the IBC

303.3 Assembly Group A-2.
Group A-2 occupancy includes assembly uses intended for food and/or drink consumption including, but not limited to:

Banquet halls

Casinos (gaming areas)

Nightclubs

Restaurants, cafeterias and similar dining facilities (including associated commercial kitchens)
 
Unless there is a fire compartment due to excessive fire area, the kitchen and dining area are both classified A-2 and no separation would typically be provided.
 