Commercial Kitchen Fire Rating in I-2 Occupancy

Does the kitchen require an fire rating separation?


  • Total voters
    1

100eyeballs

Bronze Member
Joined
Sep 7, 2011
Messages
45
Location
Michigan
Is a kitchen serving more than 30 occupants in an I-2 occupancy considered a hazardous use that needs a fire rating separation? Example: Large hospital.
 
Not sure what NFPA 101 would require, but a commercial kitchen without an associated dining area is typically classified as a Group F-1. This is more explicit in the 2015 IBC. If separated occupancies are required, then a 2-hour fire barrier is needed to separate the Group F-1 from the Group I-2 per Table 508.4. If it can be considered an accessory occupancy, then no separation is required.
 
  • Like
Reactions: JBI
Under what Code and which year edition? That will make a difference.
Being that most Hospital kitchens are associated with a dining room area, I'd say A-2 is appropriate.
Lacking a dining area, and under the 2015 IBC, I'd agree with Ron (RLGA) that F-1 would be appropriate and separation from the Hospital, in accordance with the table, would be 2 hours.
Back in the day of NYS's rogue code, we would have required 2 hours between any commercial kitchen and the dining area (or other parts of the building) regardless of occupancy category.
 