Attached (I hope) is a common entry to a B and R-3 occupancy, unsprinklered. Since the B is a higher hazard then the R-3, does wall #1 need the 2 hour separation from the common entry (exit access)? Or can I make wall #2 the 2 hour separation instead? Or would both need the 2 hour separation? Thank you.COMMON ENTRY.JPG Thanks!
 
Either, if you're using the separated occupancies method. However, if the area of the entire building does not exceed the allowable area for a Group B occupancy per the construction type, then the nonseparated occupancies method can be used and only a 1-hour fire partition is required between the Group R-3 and the Group B, and, in that case, Wall #2 would be the fire partition.
 
Further, if the separated occupancies method is used, and Wall #1 was made the 2-hour fire barrier, then Wall #2 would still have to be a 1-hour fire partition; but, if Wall #2 was the 2-hour fire barrier, then Wall #1 would not require any fire rating.
 
Thank you. The # of stories of the building (3) exceeds the allowable for the B occupancy (2), so I must use separated occupancy method. Ron, I am enjoying your book btw!
 
Thank you. The # of stories of the building (3) exceeds the allowable for the B occupancy (2), so I must use separated occupancy method. Ron, I am enjoying your book btw!
Thanks.

There are other options to look at, but some assumptions I want to confirm first before offering any include:
  • The building is sprinklered per NFPA 13R (you can't have an unsprinklered building with a Group R occupancy).
  • The construction type is VB.
  • Stories 2 and 3 are part of the Group R-3 and there are no Group B occupancies on those stories.
Please correct me if I'm wrong on any of the above.
 
So

What is the R-3???

And

Is it existing??



  • Buildings that do not contain more than two dwelling units

  • Boarding houses (nontransient) with 16 or fewer occupants

  • Boarding houses (transient) with 10 or fewer occupants

  • Care facilities that provide accommodations for five or fewer persons receiving care

  • Congregate living facilities (nontransient) with 16 or fewer occupants

  • Congregate living facilities (transient) with 10 or fewer occupants

  • Lodging houses with five or fewer guest rooms
 
I would prefer to see wall #1 rated because it would afford extra protection for those existing the R-3 if the fire was in the B occupancy
 
Thanks for the replies.....Ron, the building is an existing unsprinklered Type VB building. I am not adding any square footage to the B occupancy and there is no B occupancy on the middle or upper floors. CDA....it is a single family dwelling above (with its entry at the B level) for the R-3. Mtlogcabin...I was thinking the same as the B is a higher hazard, but I also have 2 interior windows in that wall so it will be an expensive upgrade I think.
 
Basement dig out to move the existing B occupancy down to street level (6' +/-) which will make it accessible, and enlarging the existing R occupancy where the B used to be.
 