I have a small midwest community fire inspector that handles the plan review for this area. We are in disagreement over common path of travel as outlined in the 2000 NFPA 101.
Small Quick Serve Restaurant. No Sprinkler system.
I attached a few documents for your help. Here’s the code section for reference:
2000 NFPA 101 - 12.2.5.1 Arrangements of Means of Egress: Exits shall be located remotely from each other and shall be arranged to minimize the possibility that they might be blocked by an emergency. Exception: A common path of travel shall be permitted for the first 20 ft from any point where serving any number of occupants and for the first 75 ft from any point where serving not more than 50 occupants.
There are two basic arguments:
I also included the “Exit Separation.jpg” to demonstrate that we meet the intent of the IBC for exit separation in a non-sprinklered building (50% of the diagonal length of the overall area served).
Small Quick Serve Restaurant. No Sprinkler system.
I attached a few documents for your help. Here’s the code section for reference:
2000 NFPA 101 - 12.2.5.1 Arrangements of Means of Egress: Exits shall be located remotely from each other and shall be arranged to minimize the possibility that they might be blocked by an emergency. Exception: A common path of travel shall be permitted for the first 20 ft from any point where serving any number of occupants and for the first 75 ft from any point where serving not more than 50 occupants.
There are two basic arguments:
- The common path is only 14’-0” long before the occupants have two (2) route choices to an exit (see attached “Common Path.jpg”). However, the reviewer views the common path as 33’-0” before the occupants have a choice between two (2) exits.
- The point where the occupant load reaches 50 persons occurs about halfway through our dining room, thereby, allowing 75’-0” for the common path for the back half of the dining room where the occupant load is less than 50 at any point (see attached “Occupant Load.jpg”)
I also included the “Exit Separation.jpg” to demonstrate that we meet the intent of the IBC for exit separation in a non-sprinklered building (50% of the diagonal length of the overall area served).