klarenbeek
REGISTERED
How many of you see a concentric termination designed for both exhaust and fresh air from an air exchanger? Prior to the 2012 IRC there were no distance restrictions between environmental air exhaust and mechanical air inlets, so I always went off manufacturer's instructions, typically 6', but some also approved a concentric termination.
M1506.2 is a new addition to the 2012 IRC, which puts restrictions on mechanical air intakes for residential, including 10' of separation between any exhaust and mechanical air intake. Since the termination violates the new code section, I'm no longer approving their use.
Anyone have issues with this yet? The manufacturer of the concentric cap left me a message today wanting to discuss.
M1506.2 is a new addition to the 2012 IRC, which puts restrictions on mechanical air intakes for residential, including 10' of separation between any exhaust and mechanical air intake. Since the termination violates the new code section, I'm no longer approving their use.
Anyone have issues with this yet? The manufacturer of the concentric cap left me a message today wanting to discuss.