• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Condensate drain inside fan-coil unit?

Yikes

Gold Member
Joined
Nov 2, 2009
Messages
3,075
Location
Southern California
Inside an apartment, there a horizontal fan-coil unit, such as a First Co. 26HX, with enclosure, mounted in a soffit below the rated ceiling. There is a primary condensate drain line that attaches to the pan, and terminates in the lavatory drain tailpiece just upstream from the lavatory P-trap, similar to this: https://www.jrsmith.com/uploads/fileLibrary/d9200.pdf

In lieu of a secondary overflow drain, there is an overflow shutoff switch.

Q1: Since the lavatory drain tailpiece has its own P-trap below it, is there any need for another trap+vent for the primary condensate line, up near the fan-coil unit in the soffit?

Q2: If the answer to #1 is "yes", can this additional trap occur inside the enclosure if it is made of PVC? (Thinking of flame spread, smoke etc. of combustible materials in plenums.)

Q3: If the answer to #2 is "yes", is an air gap or vent required, or is the condensate drain pan itself a type of air gap, even in the presence of negative pressure in the HVAC enclosure?
 