Curious on how other jurisdictions handle this scenario. We enforce I-codes but also must enforce NFPA from state level. There is some disagreement on how the "most restrictive" code is applied.
Lets say we have an assembly occupancy. NFPA calculated occupant load is 110. Since it is under the 300 requirement for sprinklers, none required. IBC calculated occupant load is 99. Since it is under the 100 requirement for sprinklers, none required. One person is saying that is not correct and you would have to apply the NFPA calculated occupant load of 110 to the IBC requirement of 100 and therefore sprinkle the building.
I disagree.
Thoughts?
Lets say we have an assembly occupancy. NFPA calculated occupant load is 110. Since it is under the 300 requirement for sprinklers, none required. IBC calculated occupant load is 99. Since it is under the 100 requirement for sprinklers, none required. One person is saying that is not correct and you would have to apply the NFPA calculated occupant load of 110 to the IBC requirement of 100 and therefore sprinkle the building.
I disagree.
Thoughts?