I'm working on a 7-story residential R-2 apartment bldg. (I've posted about it before).
I'm using provision 510.2 for a podium bldg. I have 2 stories below (S-2 parking garage, lobby and fitness), and 5 stories above. The building above the podium is all R-2, we have indoor/outdoor roof decks (each space under 750sf, so classified as R-2) (at least for now until the client increases the size of the rooftop amenity).
The building height is 79'-6" from grade plane to avg roof. Our floor plate per floor is about 10,800 for floors 3 - 6, and floor seven is about 9,000 (don't have actual #s on me at this time), in round numbers 52,000 total.
It appears to me the project works under IIB. Height allowed is 75', so we comply. Stories is 5 for either A or B, so OK. Allowable area is 48,000, so times 3 = 144,000sf. divided by 5 stories I'm allowed about 28,000 sf, without even taking anything for frontage. So we comply.
Usually in my office when we do these types of projects I expect a 1hr rating at floors and apartment walls, and exterior walls too, though many of our buildings are wood. Are there other provisions that I should watch out for that could kick me up to IIA? Or am I good? I haven't worked on a project that's had basically no ratings so want to make sure I'm not missing something.
If so, I basically have no rating requirements. Our building is load-bearing steel stud walls, we're using a UL between apartments which is already 2 hr (we're using it because the owner wants STC of 60). We had been planning to use UL G548 for the floors. So we could drop the Type X GWB, and use non-rated dampers and such for the ductwork going through this assembly?
For exterior walls, all my fire separation distances are more than 10' (mostly to centerline of street, one side on park with no-build easement). So, per Table 602 I have no required rating for IIB either.
Seems too good to be true - am I missing something?
Thanks
I'm working on a 7-story residential R-2 apartment bldg. (I've posted about it before).
I'm using provision 510.2 for a podium bldg. I have 2 stories below (S-2 parking garage, lobby and fitness), and 5 stories above. The building above the podium is all R-2, we have indoor/outdoor roof decks (each space under 750sf, so classified as R-2) (at least for now until the client increases the size of the rooftop amenity).
The building height is 79'-6" from grade plane to avg roof. Our floor plate per floor is about 10,800 for floors 3 - 6, and floor seven is about 9,000 (don't have actual #s on me at this time), in round numbers 52,000 total.
It appears to me the project works under IIB. Height allowed is 75', so we comply. Stories is 5 for either A or B, so OK. Allowable area is 48,000, so times 3 = 144,000sf. divided by 5 stories I'm allowed about 28,000 sf, without even taking anything for frontage. So we comply.
Usually in my office when we do these types of projects I expect a 1hr rating at floors and apartment walls, and exterior walls too, though many of our buildings are wood. Are there other provisions that I should watch out for that could kick me up to IIA? Or am I good? I haven't worked on a project that's had basically no ratings so want to make sure I'm not missing something.
If so, I basically have no rating requirements. Our building is load-bearing steel stud walls, we're using a UL between apartments which is already 2 hr (we're using it because the owner wants STC of 60). We had been planning to use UL G548 for the floors. So we could drop the Type X GWB, and use non-rated dampers and such for the ductwork going through this assembly?
For exterior walls, all my fire separation distances are more than 10' (mostly to centerline of street, one side on park with no-build easement). So, per Table 602 I have no required rating for IIB either.
Seems too good to be true - am I missing something?
Thanks