wwhitney
REGISTERED
The 2023 NEC and the 2021 IBC have very similar definitions of "Structure":
2021 IBC "STRUCTURE. That which is built or constructed."
2023 NEC "Structure. That which is built or constructed, other than equipment."
The NEC added that last clause "other than equipment" in the 2017 version to clarify, for example, that if you run a feeder to a free-standing self-contained power pedestal set in the middle of a field, it is equipment only, therefore not a structure, and therefore does not require a grounding electrode system. [If you instead use a panelboard on a 4x4 post in the ground, it is still a bit ambiguous whether the 4x4 post is equipment or not; if not, that is a structure and would require a grounding electrode system.]
However, the 2023 NEC and 2021 IBC have very different definitions of "Building":
2021 IBC "BUILDING. Any structure utilized or intended for supporting or sheltering any occupancy."
2023 NEC "Building. A structure that stands alone or that is separated from adjoining structures by fire walls."
[Apparently the NEC is happy to call a flagpole or a human-scale sculpture a building, but the IBC does not wish to do that.] The main distinction the NEC is making between structures and buildings is that bit about firewalls. For the NEC a series of townhouses separated by firewalls would be one structure but multiple buildings; and so for example when 230.2 says in effect "one service per building," that automatically allows one service per townhouse without requiring any exception or other language.
My question is a basic one about the IBC, with which I'm not so familiar, particularly its fire requirements. What is the IBC equivalent term for the way the NEC is using the term "Building"? I.e. a portion of a structure which is separated by (sufficiently rated) firewalls?
Thanks,
Wayne
2021 IBC "STRUCTURE. That which is built or constructed."
2023 NEC "Structure. That which is built or constructed, other than equipment."
The NEC added that last clause "other than equipment" in the 2017 version to clarify, for example, that if you run a feeder to a free-standing self-contained power pedestal set in the middle of a field, it is equipment only, therefore not a structure, and therefore does not require a grounding electrode system. [If you instead use a panelboard on a 4x4 post in the ground, it is still a bit ambiguous whether the 4x4 post is equipment or not; if not, that is a structure and would require a grounding electrode system.]
However, the 2023 NEC and 2021 IBC have very different definitions of "Building":
2021 IBC "BUILDING. Any structure utilized or intended for supporting or sheltering any occupancy."
2023 NEC "Building. A structure that stands alone or that is separated from adjoining structures by fire walls."
[Apparently the NEC is happy to call a flagpole or a human-scale sculpture a building, but the IBC does not wish to do that.] The main distinction the NEC is making between structures and buildings is that bit about firewalls. For the NEC a series of townhouses separated by firewalls would be one structure but multiple buildings; and so for example when 230.2 says in effect "one service per building," that automatically allows one service per townhouse without requiring any exception or other language.
My question is a basic one about the IBC, with which I'm not so familiar, particularly its fire requirements. What is the IBC equivalent term for the way the NEC is using the term "Building"? I.e. a portion of a structure which is separated by (sufficiently rated) firewalls?
Thanks,
Wayne