I posted this with part of another thread, but need some help to confirm please.
Table 1018.1 allows a corridor not to be rated if a B occupancy and with a sprinkler system. Can a corridor be non-rated if one means of egress goes through the elevator lobby that maintains it's one hour rating with 20 minute smoke doors (1A construction high-rise). Does passing through the elevator lobby for egress require that the 1 hour rating be continued or would the exception that says the "corridors may lead through enclosed elevator lobbies if all areas of the building have access to at least one required exit without passing through the elevator lobby".
My interpretation of this is that the corridor does not need to be rated just because it passes through a rated elevator lobby. My plan checker says it does.
Thoughts?
Table 1018.1 allows a corridor not to be rated if a B occupancy and with a sprinkler system. Can a corridor be non-rated if one means of egress goes through the elevator lobby that maintains it's one hour rating with 20 minute smoke doors (1A construction high-rise). Does passing through the elevator lobby for egress require that the 1 hour rating be continued or would the exception that says the "corridors may lead through enclosed elevator lobbies if all areas of the building have access to at least one required exit without passing through the elevator lobby".