Mech
REGISTERED
2009 IBC
No sprinklers
Restaurant A-2 with passageway / hallway providing a path of travel to the restrooms, a private office, and the second required exit. Occupant load is greater than 30. If the passageway / hallway wall stops two or three feet from the ceiling, must it be considered a corridor and be fire rated? There are no dead ends.
1018.1 Construction. Corridors shall be fire-resistance rated in accordance with Table 1018.1. The corridor walls required to be fire-resistance rated shall comply with Section 709 for fire partitions.
Table 1018.1 requires a one-hour corridor rating for occupant loads greater than 30 in Assembly occupancies without sprinklers.
Thanks in advance.
No sprinklers
Restaurant A-2 with passageway / hallway providing a path of travel to the restrooms, a private office, and the second required exit. Occupant load is greater than 30. If the passageway / hallway wall stops two or three feet from the ceiling, must it be considered a corridor and be fire rated? There are no dead ends.