Dr. J - the "30 square feet or less" is in the 2010 California modifications to the IBC. I agree that we can no longer utilize building infiltration, both from a code standpoint and from real-world conditions.brudgers - the requirements for smoke seals at corridors doors are for the top and sides of the door opening, not the threshold.
That leaves the question of its fire resistance:
The maximum undercut of a fire rated door per is 3/8" at the bottom edge IBC / CBC Referenced standard 12-7-404(b)9 for "fire door assembly tests", which states:
9. Clearances for swinging doors shall be (with a minus 1/16-inch tolerance) as follows: 1/8 inch along the meeting edge of doors in pairs, 3/8 inch at the bottom edge of single swing doors and 1/4 inch at the bottom edge of a pair of doors.
On a typical 36" wide door, a 3/8" clearance x 36" width = 13.5 max. square inches, roughly equivalent to a 4" diameter bath exhaust vent.