Hello all..
Just FYI, I'm using NYS Version of I-codes and have a question on the verbage within 1016.2 Exception 4.
4. Seventy-two inches (1829 mm)—In Group E with a corridor having a required capacity of 100 or more.
What's with the word "required" in there?
This is my situation, I have a corridor, constructed @ 66 inches, Group E (obviously). It's for a preschool type occupancy. Corridor wraps around the buidling, occupant load is
162 Children
27 Teachers
2 office staff
191 Total.
All classrooms have exits to outside, buidling sprinklered. Stumbled on 6 foot width verbage during the "final" inspection.
I read the code as where the corridor is serving 100 or more, it needs to be a minimum 72 inches.
Anyone clarify?
Thanks.