Cover it with a picture

  • Thread starter Thread starter -
  • Start date Start date

Guest
The service panel is mounted over a sheet of steel and the previous service cabinet is still in the wall and is now a j-box. One of the corrections I wrote was to relocate the new cabinet and make the j-box accessible. The second picture is the result. It is in a bedroom behind a picture.




 
Last edited by a moderator:
Re: Cover it with a picture

Are you sure you live in California. Most of the time I always hear how strict the building code is out there but it looks like you may not have had one before you started working there. :D
 
Re: Cover it with a picture

tigerloose said:
One of the corrections I wrote was to relocate the new cabinet and make the j-box accessible.
If this permit was pulled under the 08 NEC I think you may have a problem with 330.10(A)(11) also.
 
Re: Cover it with a picture

That is not MC cable. It is a bare #6 grounding electrode conductor in armor.
 
Re: Cover it with a picture

tigerloose said:
That is not MC cable. It is a bare #6 grounding electrode conductor in armor.
Where does the GEC that goes up go?

Also, thanks Jeff, I'll start putting the text with any NEC references.
 
Re: Cover it with a picture

Where does the GEC that goes up go?

It goes into the attic and across the house and down to the water main.

And no Jeff, we don't have Polish water mains.
 
Re: Cover it with a picture

That one picture is an "Arkansas wall safe" that's were you store your gun and baseball cards!
 