In one-hour fire-resistance rated floor assemblies, the ceiling membrane is not required to be installed over unuseable crawl spaces. Section 712.3.3.
If the celing membrane is not required even when the floor assembly is required to be a fire-rated asemblies, why would it be required for non rated assemblies? This is of course assuming that the crawl space is actually a crawl space and not a useable space.
If the celing membrane is not required even when the floor assembly is required to be a fire-rated asemblies, why would it be required for non rated assemblies? This is of course assuming that the crawl space is actually a crawl space and not a useable space.