Would this bonding be allowed on a CSST gas line. The bounding wire is on the steel gas pipe and not on the brass fitting connector?
No.Require a test of the ground?
No.
Solid #6 attached upstream of the CSST and taken to the grounding electrode system.
There is a CSST manufacturer that makes the claim that their CSST has been Listed without the addition bonding jumper. I haven't seen the Listing so I don't know for sure.
When this material came on the market a certification was required to install or inspect it. That has changed up to "anybody can do both". Sometimes I ask for the installation instructions.....they discover a forty page document.....with striker plates......and change to hard pipe.
I think it is the black csst, May have a continuous ground, through the length of the pipe
When some entity decides to list a clamp for a particular type of material what is the criteria they use?
(I particularly appreciated his story on the importance of sleeving the CSST where it passes thru the sidewalls of Fireplace Inserts.)
Apparently there is no technical criteria for listing a clamp. This lack of criteria suggests that there is no rational basis for requiring clamps be listed. So why is a listing being required.
If you are concerned about bonding thein you could resolve the question by measuring the resistance. There will always be some resistance so you cannot say zero.. The question is what is an acceptable value?