Tracpipe Installation Instructions:Notes:
a. If possible, avoid running the bonding
jumper a long distance through the
building. The connection should be as
short as possible. Gas meter should
be near the electrical service if possible.
If not, the bond can be connected
at any point near the electrical serviceper Figure 4-21.
Tracpipe is commonly used in my location. If the gas meter is a long distance from the electrical service, connecting the CSST near the electrical service takes priority over connecting at the gas service point-of-entry.