2007 Florida Mechanical: Situation: A 3 story building, Mixed occupancy: A-3 and E (church and school). Type 1B construction. Table 601 requires 3 hour rated exterior or interior bearing walls. The walls are 9" thick concrete tilt-up walls, similar to UL926, which requires only a minimum of 6" precast concrete wall for 4 hour rating. At 9' thickness (50% over) we could conceivable be up to 6 hour rating with this if thickness and ratings were on a linear scale.
The question: In locations where this wall happens to separate an exit corridor from another function (class or office, for example), is the damper required for a duct penetration as required for the corridor (1 hour), as required for the bearing wall (3 hour), as for the rating claimed by the UL rating (4 hour) on the plans for this wall, or as the rating provided by the built unit (possibly 6 hour)?
If the answer is "as required for the bearing wall", then I assume it can also be reduced to 2hr per footnote "b" on the upper floor.
Problem: the Mechanical inspector is saying "3 hour wall = damper rated for 3hr wall"
The question: In locations where this wall happens to separate an exit corridor from another function (class or office, for example), is the damper required for a duct penetration as required for the corridor (1 hour), as required for the bearing wall (3 hour), as for the rating claimed by the UL rating (4 hour) on the plans for this wall, or as the rating provided by the built unit (possibly 6 hour)?
If the answer is "as required for the bearing wall", then I assume it can also be reduced to 2hr per footnote "b" on the upper floor.
Problem: the Mechanical inspector is saying "3 hour wall = damper rated for 3hr wall"