Re: Dead end corridor = 20 feet
OK, I will, at the risk of making a backside of my self, assume that the following 2 interpretations still exist in the 2006 book of interpretations (someone borrowed mine last week and believes it was a gift - it wasn't!). So somebody here can verify if they are still there.
From the 2000 & 2003 interp books:
Q: Does Section 1016 [1017 in 2006] require exit access corridors to be provided in buildings?A: No. Section 1016 [1017 in 2006] only provides requirements for exit access corridors whenever they are provided in a building. The International Building Code requires access to exits for every building, which can be accomplished by open spaces, aisles or corridors. A corridor is created when the path of travel to an exit is confined, and communication with and observation of adjacent floor areas are restricted.
and, though fire-rated, this is similar
Q: A floor plan, of which a portion is an open plan without corridors and an adjacent portion that is compartmented, contains a corridor that leads to the open plan area. Assuming the corridor enclosure is required to be fire-resistance rated, is it the intent of the code to require that an opening protective be installed at the point where the corridor enters the open area?A: No. The relatively open areas adjacent to the corridor can be considered corridor extensions with rated walls and opening protectives enclosing both the narrow and wide portions of the corridor in a continuous fashion
and from the 2006 commentary for definition of a corridor:
Corridors have walls that extend from the floor to at least the ceiling. They need not extend above the ceiling or have doors in their openings unless a fire-resistance rating is required (see Section 1017). The enclosed character of the corridor restricts the sensory perception of the user. A fire located on the other side of the corridor wall, for example, may not be as readily seen, heard or smelled by the occupants traveling through the egress corridor.
and more from the 2006 commentary for dead ends:
A dead end results whether or not egress elements open into it. A dead end is a hazard for occupants who enter the area from adjacent spaces, travel past an exit into a dead end or enter a dead end with the mistaken assumption that an exit is directly accessible from the dead end.
I know that all this crap I quoted is not code, but, food for thought in making a judgment.
My judgment is that it is a corridor, no rating as the corridor serves an occupant load less than 30 (coming from the toilet rooms), door is not required at the end of the corridor, not a dead end because it starts at the toilet room wall - less than 20' long.
Now as far as that stair is concerned, I might look at 1019.3 and 1020.1 exception 8 or apply the last sentence in 3406.1.