Ok I have another contractor disagreeing with my interpretation of code intent.
I cannot find any reference to deck rail construction except the table R301.5 requires 200 lb/sqft as live load on guardrails and handrails.
I failed this deck twice. 16x10 deck and the 16' side of the deck having one rail in the middle, 8' span between posts. This post was attached to the band joist with lag screws that did not protrude through, so I had no idea how deep it was into the band. I also could flex the band board by moving the top of the post more than an inch without much effort.
So he replaces the lags with through carriage bolts, which may be another issue as I believe washers inside and out are needed. But he did not address the flexing of the band with either brackets per DCA6 or some type of blocking to decrease the deflection. He comes in to discuss the failure as he doesn't understand why this failed. He stated that he put 200lbs of force on the rail and it deflected 3.5" and did not fail so it meets code!!
My response was that it should not deflect that much but did not have an immediate answer for an allowable amount of deflection. He agreed to install a bracket per DCA 6 and left. But I really would like to understand what an allowable amount of deflection is commonly accepted so I may better enforce the rails being installed on decks.
I spoke with several engineers and also did some research online and it was unanimous that the formula H/60 was commonly used for rail deflection design. This was referenced to 1604.3 in the IBC as a cantilevered member. I'm not quite clear how they arrive at that but as it was an acceptable criteria for my building official.
Well after much time spent on this one answer I have come here with several different schools of thought on the matter with hopes of some wise advice from my fellow code geeks LOL.
I personally like the common engineered practice of H/60. I have found the ICC test standard for rails AC273 but it seems to allow about 2.5" of deflection on the rail system. I am confused by the report as it states to apply 500lbs but measure the deflection at 200lbs. 2.5" at 200lbs seems very excessive to me, anyone else? This morning I have found a chart in the IRC, table R301.7 that has "All other structural members" L/240 as maximum deflection. This is right after the live loads chart. That is even more restrictive so I'm just so confused. HELP!!
So the numbers look like this:
Engineer 36"(H)/60 = .60 deflection
AC273 36"(H)/24+96"(L)/96 = 2.5" of deflection on midpoint Link to AC273
IRC table 72"(H)/240 = .30 of deflection (72" per footnote b, L shall be twice the cantilever length.)
So am I putting too much thought into this or what? I'm sorry but the perception for many is the reality and the homeowner was terrified at the amount of movement in the rail. As was I when I did the throw a hip into it test and felt like I was going fall off the deck! I feel that 1/2" to 1" of deflection at 200lbs should be sufficient to meet the intent of code when it comes to the safety of guardrails.
Thoughts?
I cannot find any reference to deck rail construction except the table R301.5 requires 200 lb/sqft as live load on guardrails and handrails.
I failed this deck twice. 16x10 deck and the 16' side of the deck having one rail in the middle, 8' span between posts. This post was attached to the band joist with lag screws that did not protrude through, so I had no idea how deep it was into the band. I also could flex the band board by moving the top of the post more than an inch without much effort.
So he replaces the lags with through carriage bolts, which may be another issue as I believe washers inside and out are needed. But he did not address the flexing of the band with either brackets per DCA6 or some type of blocking to decrease the deflection. He comes in to discuss the failure as he doesn't understand why this failed. He stated that he put 200lbs of force on the rail and it deflected 3.5" and did not fail so it meets code!!
My response was that it should not deflect that much but did not have an immediate answer for an allowable amount of deflection. He agreed to install a bracket per DCA 6 and left. But I really would like to understand what an allowable amount of deflection is commonly accepted so I may better enforce the rails being installed on decks.
I spoke with several engineers and also did some research online and it was unanimous that the formula H/60 was commonly used for rail deflection design. This was referenced to 1604.3 in the IBC as a cantilevered member. I'm not quite clear how they arrive at that but as it was an acceptable criteria for my building official.
Well after much time spent on this one answer I have come here with several different schools of thought on the matter with hopes of some wise advice from my fellow code geeks LOL.
I personally like the common engineered practice of H/60. I have found the ICC test standard for rails AC273 but it seems to allow about 2.5" of deflection on the rail system. I am confused by the report as it states to apply 500lbs but measure the deflection at 200lbs. 2.5" at 200lbs seems very excessive to me, anyone else? This morning I have found a chart in the IRC, table R301.7 that has "All other structural members" L/240 as maximum deflection. This is right after the live loads chart. That is even more restrictive so I'm just so confused. HELP!!
So the numbers look like this:
Engineer 36"(H)/60 = .60 deflection
AC273 36"(H)/24+96"(L)/96 = 2.5" of deflection on midpoint Link to AC273
IRC table 72"(H)/240 = .30 of deflection (72" per footnote b, L shall be twice the cantilever length.)
So am I putting too much thought into this or what? I'm sorry but the perception for many is the reality and the homeowner was terrified at the amount of movement in the rail. As was I when I did the throw a hip into it test and felt like I was going fall off the deck! I feel that 1/2" to 1" of deflection at 200lbs should be sufficient to meet the intent of code when it comes to the safety of guardrails.
Thoughts?