(IBC 2012, Washington, D.C., 2-story existing building renovation, construction type 2B, Use Group B.)
I've been asked to determine if it's allowable to have a decorative wood ceiling element within a fire-rated corridor and fire-rated stair? We have a fire rated corridor on second floor, fire-rated egress stair to first floor, and a fire-rated lobby acting as the egress corridor to the exterior exit. All three of these spaces are proposed to have the decorative wood elements. For simplicity's sake picture them as wood 1x4's spanning in one direction across each space, flat side placed horizontally, spaced about 1/2" apart. Obviously fire sprinklers would need to penetrate through these. But the big question is, would this be allowed at all?
If possible please direct me to any code sections that show it being allowed or not. I'm looking at IBC 806 but it doesn't seem to directly address my condition. Thanks!
I've been asked to determine if it's allowable to have a decorative wood ceiling element within a fire-rated corridor and fire-rated stair? We have a fire rated corridor on second floor, fire-rated egress stair to first floor, and a fire-rated lobby acting as the egress corridor to the exterior exit. All three of these spaces are proposed to have the decorative wood elements. For simplicity's sake picture them as wood 1x4's spanning in one direction across each space, flat side placed horizontally, spaced about 1/2" apart. Obviously fire sprinklers would need to penetrate through these. But the big question is, would this be allowed at all?