310.15(B)(5)(a)
A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(3)(a).
Contractors and others want to apply this to every shared neutral. That neutral has the potential to carry an unbalanced load as is the case for a multiwire branch circuit that feeds lighting or a duplex receptacle for a dishwasher and garbage disposal.
Alrighty then, is the potential to carry an unbalanced load the same as "only the unbalanced load"? I say no. The logical use of a multiwire branch circuit is that it will usually not carry an unbalanced load. And if it has the potential to carry neutral current from just one line then it does not qualify for elimination when counting the current carrying conductors.
What say you?
A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(3)(a).
Contractors and others want to apply this to every shared neutral. That neutral has the potential to carry an unbalanced load as is the case for a multiwire branch circuit that feeds lighting or a duplex receptacle for a dishwasher and garbage disposal.
Alrighty then, is the potential to carry an unbalanced load the same as "only the unbalanced load"? I say no. The logical use of a multiwire branch circuit is that it will usually not carry an unbalanced load. And if it has the potential to carry neutral current from just one line then it does not qualify for elimination when counting the current carrying conductors.
What say you?