Designated aisle seats per California Accessibility
In the image I posted, the slope is a maximum of 6 percent and that slope occurs beyond the designated aisle seats towards the screen so that the walking surface to the seats is less than six percent. The theater has no stairs. I'm trying to understand why the designated aisle seats are not compliant.
Is there a level landing adjacent to the Designated aisle seats?
is there the proper maneuvering space adjacent to the Designated aisle seats?
mark handler said:
Is there a level landing adjacent to the Designated aisle seats?is there the proper maneuvering space adjacent to the Designated aisle seats?
Why does there need to be a landing and/or maneuvering space when this is not for a wheelchair space? Here's an elevation of the theater with the yellow marks indicating the locations of the designated aisle seats. View attachment 764
/monthly_2013_07/Capture1.PNG.1d788ac4efbc9e8f0422d067074a8170.PNG
There is no need for a level landing or maneuvering space adjacent to the aisle seats. They should be the closest end of aisle seats to the accessible path. In this case it looks like they should be the first three rows at the top closest to the accessible path unless there is also a path at the front of the seating area.
How does a side transfer work?
these are not "the Seating for semi-ambulant individuals" what I am referring to is the required "Designated aisle seats" separate requirement
thank you Code Geek for your patience and allowing me to learn a new code requirement that i am not familiar with. I have been out of the building department side with accessibility for almost 7 years.... this requirement took me by surprise... thus the steep learning curve for me from this board.
The post is dealing with the CBC
mark handler said:
There is no need for a level landing or maneuvering space adjacent to the aisle seats. How does a side transfer work?
Designated aisle seats are not intended to accommodate a side transfer.
Headquarters Office
1102 Q Street, Suite 5100 | T 916.445.8100
Sacramento, CA 95811 | F 916.445.3521
DSA Home
Sacramento Oakland Los Angeles San Diego
Regional Office Regional Office Regional Office Regional Office
1102 Q Street, Suite 5200 1515 Clay Street, Suite 1201 700 N. Alameda St., Suite 5-500 10920 Via Frontera, Suite 300
Sacramento, CA 95811 Oakland, CA 94612 Los Angeles, CA 90012 San Diego, CA 92127
T 916.445.8730 T 510.622.3101 T 213.897.3995 T 858.674.5400
25 July 2012
Access Compliance Emergency Regulations
The Building Standards Commission approved DSA’s Access Compliance
Emergency Regulations Package on July 19, 2012. These regulations will be
effective on August 1, 2012. The Emergency Regulations:
 Resolve a very limited number of direct conflicts between the 2010 CBC and the
2010 ADA Standards.
 Correct a typographical error in the 2010 Supplemental rulemaking package that
went into effect on July 1, 2012.
 Provide for acceptance of select previously compliant elements along a path of
travel.
A summary of the Emergency Regulations items, along with their corresponding
2010 California Building Code Chapter 11B section numbers, is provided below to
clarify their application to the design and construction of projects.
Item 1 – 1104B.3.9 Designated aisle seats
 Correction of a typographical error during the 2010 rulemaking cycle.
 The intent was to align with the ADA Standards Section 221.4 Designated
Aisle Seats, which calls for 5 percent of aisle seats to be designated aisle
seats.
 The faulty language would have required 5 percent of fixed seats to be
designated aisle seats, possibly 20 or more times the number required by the
2010 ADA Standards or intended by the code revision.
 The Emergency Regulations correct this error.
It should be noted that designated aisle seats are not intended to be used as
transfer seats for wheelchair users nor are they required to be on an
accessible route; they are, however, required to be the aisle seats closest to
the accessible route serving their aisle.
Item 2 – 1115B.4.1 Accessible Water Closets
 Prior 2010 CBC language required an absolute dimension of 18” from the
centerline of the water closet to the adjacent side wall.
Not inserted the way I would like but the info should be in bold, Direct from DSA,
note: it did not bold, look for notation between my added where it says........... It should be noted that designated aisle seats are not intended to be used as