"Groups of disconnects" spread out along the exterior wall; what limits the distance between them?
Francis
Francis
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Your feet.Francis Vineyard said:"Groups of disconnects" spread out along the exterior wall; what limits the distance between them?Francis
Could it be that when you run it on the exterior or underground that if there was a short circuit there would be less chance of a fire considering the limited overcurent protection from the POCODennis said:I agree with North Star but I am not sure if these disconnects are on the exterior wall inside or outside. If you have 6 meters and the service entrance conductors are run outside the building then there is no limit on the length of the conductors. It changes once you enter the building and states as near as possible to the point of entry. Some areas have amendments that allow "X" feet. The NEC gives no length. 230.70(A)(1)In terms of the grouping that is totally arbitrary. Obviously if the wall is 100 feet long and you have them spread out the entire length then that may be an issue--Obviously the size of the disconnects can keep them apart but how far apart is too far is anyone's call.
It seems the reason I hear is so the FD can get to it quickly. Well that theory is ridiculous when you consider the fact that I can have the meters on one side of the building and the disconnects on the opposite end if I run the services wires on the exterior or below grade.
Sure, that is why it is allowed on the exterior in unlimited length but not why they must be grouped.Gregg Harris said:Could it be that when you run it on the exterior or underground that if there was a short circuit there would be less chance of a fire considering the limited overcurent protection from the POCO
I disagree for the reasons stated above.codeworks said:grouping is so that in an emergency ( fire, collapse, etc) emergency personnel can go to one location and kill the power rthey need to ( all or some, whatever the situation dictates