Do sprinklers reduce required fire ratings?

Mech

REGISTERED
Joined
Oct 30, 2009
Messages
1,054
Location
Eastern PA
2000 NFPA 101

2009 IBC Chapter 34 or 2009 IEBC

Existing Health Care Facility with sprinklers

I need to re-establish a smoke barrier with either a 1/2 hour or 1 hour fire rating. Is there an exception that reduces or eliminates the required fire rating due to the fire suppression system? I skimmed the code quickly but did not find anything.

Thanks
 
one problem is you have to go with the stricter of the codes

what is this seperating??
 
A Smoke barrier by definition must be a one hour assembly where a smoke partition has no rating. The only reduction I'm seeing is for an I-3 building with a minimum of 0.1 inch thick steel in Section 710.3.
 
what is this separating??
Compartmentation of the building.

I just spoke with a former code reviewer and it seems that in a nursing home, the health department would not relax those rules.

I am going to suggest to the client that we pay for a preliminary review and discuss the possible options with a code reviewer before we waste too much time or money.

Thanks for the info.
 
CG got it.....If it needs to be a smoke barrier....Sprinklers can reduce for corridors and rated structure and some others, but nothing under 709 for SB's....
 