1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Do sprinklers reduce required fire ratings?

Discussion in 'Institutional' started by Mech, Mar 4, 2014.

  1. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    802
    Likes Received:
    26
    2000 NFPA 101

    2009 IBC Chapter 34 or 2009 IEBC

    Existing Health Care Facility with sprinklers

    I need to re-establish a smoke barrier with either a 1/2 hour or 1 hour fire rating. Is there an exception that reduces or eliminates the required fire rating due to the fire suppression system? I skimmed the code quickly but did not find anything.

    Thanks
     
  2. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,929
    Likes Received:
    1,102
    one problem is you have to go with the stricter of the codes

    what is this seperating??
     
  3. Codegeek

    Codegeek Registered User

    Joined:
    Jun 17, 2011
    Messages:
    717
    Likes Received:
    1
    A Smoke barrier by definition must be a one hour assembly where a smoke partition has no rating. The only reduction I'm seeing is for an I-3 building with a minimum of 0.1 inch thick steel in Section 710.3.
     
  4. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    802
    Likes Received:
    26
    Compartmentation of the building.

    I just spoke with a former code reviewer and it seems that in a nursing home, the health department would not relax those rules.

    I am going to suggest to the client that we pay for a preliminary review and discuss the possible options with a code reviewer before we waste too much time or money.

    Thanks for the info.
     
  5. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,785
    Likes Received:
    964
    CG got it.....If it needs to be a smoke barrier....Sprinklers can reduce for corridors and rated structure and some others, but nothing under 709 for SB's....
     
  6. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,929
    Likes Received:
    1,102
    I think 101 is going to be your problem
     
  7. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,827
    Likes Received:
    598
    Usually is.............
     
  8. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    802
    Likes Received:
    26
    The code is not the problem . . . making a butchered building comply with it is.
     
  9. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,929
    Likes Received:
    1,102
    Ohhhhhhhhh
     