thriftwoo
REGISTERED
This change was made to the 2018 IBC, Section 503.1:
[…] For the purposes of determining area limitations, height limitations and type of construction, each portion of a building separated by one or more fire walls complying with Section 706 shall be considered to be a separate building.
Example: Three attached F-1 tenant spaces on a single property. Each tenant space has a 10,000 sf fire area and is separated from the other F-1 tenants by 3-hour fire walls. In IBC 2015, each tenant space can be evaluated as a separate building for calculating combined fire areas. In this case, sprinklers would not be required per IBC 903.2.3, as no single building has a combined fire area exceeding 24,000sf.
I interpret the literal text of the 2018 IBC change to mean that fire walls now only create separate buildings in regard to height and area limitations and type of construction under chapter 5. In evaluating combined fire areas, you cannot consider the three tenants as separate buildings, regardless of the presence of fire walls. In this example, the combined fire areas would be 30,000 sf, requiring sprinklers throughout all three tenant spaces per IBC 903.2.3.
Digging into the committee action associated with this change (see below), it seems the intent of the change was to reduce duplication of building systems from building officials assuming each “building” on either side of a fire wall requires completely separate systems. It doesn’t appear to be the intent to prevent using fire walls to split up buildings to keep combined fire areas below the areas triggering sprinklers.
G 130-15
503.1, 706.1
2015 International Building Code
Revise as follows:
503.1 General. Unless otherwise specifically modified in Chapter 4 and this chapter, building height, number of stories and building area shall not exceed the limits specified in Sections 504 and 506 based on the type of construction as determined by Section 602 and the occupancies as determined by Section 302 except as modified hereafter. Building height, number of stories and building area provisions shall be applied independently.EachFor the purposes of determining area limitations, height limitations and type of construction, each portion of a building separated by one or more fire walls complying with Section 706 shall be considered to be a separate building.
706.1 General.Each portion of a building separated by one or more fire
Fire wallsthat comply with the provisions of this section shall be considered a separate buildingconstructed in accordance with Sections 706.2 through 706.11. The extent and location of such fire walls shall provide a complete separation. Where a fire wall separates occupancies that are required to be separated by a fire barrier wall, the most restrictive requirements of each separation shall apply.
Reason: The purpose of this proposal is to clarify the intent of these sections of the Code that the requirement for a fire wall in Sections 503.1 and 706.1 is predicated on the determination of the maximum allowable height and area calculations under Chapter 5. Using these sections of Code to control other building features or elements such as means of egress, building systems or building utilities is not intended or implied by these sections of the Code. However, by inclusion of the first sentence in Section 706.1 some code officials have incorrectly interpreted that language to mean that the portions of the various elements and systems on each side of a fire wall must be completely self-contained. There are no requirements in the I Codes that mandate that the placement of fire walls to create a separate building such that its building features need to be separated from other like building features in adjacent buildings. The scope of Section 706 is to provide the technical requirements for the construction of a fire wall.
The added language in Section 503.1 along with the strikeout and added language in Section 706.1 will clarify application of these two sections.
G 130-15 Committee Action:
Approved as Submitted
Committee Reason: The proposal clearly separates the scoping of fire walls from the design requirements for fire walls. Section 706.1 is the location of the standards for fire walls and is similar other provisions in Chapter 7 which are the 'cook books' for each type of wall and horizontal assemblies. The committee hopes that this will reduce requests for duplication of other systems such as sprinkler systems, electrical systems, etc, in each portion of a structure separated by fire walls. The new text in 503.1 clearly states why fire walls are needed for addressing height and area limitations as well as type of construction.
[…] For the purposes of determining area limitations, height limitations and type of construction, each portion of a building separated by one or more fire walls complying with Section 706 shall be considered to be a separate building.
Example: Three attached F-1 tenant spaces on a single property. Each tenant space has a 10,000 sf fire area and is separated from the other F-1 tenants by 3-hour fire walls. In IBC 2015, each tenant space can be evaluated as a separate building for calculating combined fire areas. In this case, sprinklers would not be required per IBC 903.2.3, as no single building has a combined fire area exceeding 24,000sf.
I interpret the literal text of the 2018 IBC change to mean that fire walls now only create separate buildings in regard to height and area limitations and type of construction under chapter 5. In evaluating combined fire areas, you cannot consider the three tenants as separate buildings, regardless of the presence of fire walls. In this example, the combined fire areas would be 30,000 sf, requiring sprinklers throughout all three tenant spaces per IBC 903.2.3.
Digging into the committee action associated with this change (see below), it seems the intent of the change was to reduce duplication of building systems from building officials assuming each “building” on either side of a fire wall requires completely separate systems. It doesn’t appear to be the intent to prevent using fire walls to split up buildings to keep combined fire areas below the areas triggering sprinklers.
G 130-15
503.1, 706.1
2015 International Building Code
Revise as follows:
503.1 General. Unless otherwise specifically modified in Chapter 4 and this chapter, building height, number of stories and building area shall not exceed the limits specified in Sections 504 and 506 based on the type of construction as determined by Section 602 and the occupancies as determined by Section 302 except as modified hereafter. Building height, number of stories and building area provisions shall be applied independently.
706.1 General.
Fire walls
Reason: The purpose of this proposal is to clarify the intent of these sections of the Code that the requirement for a fire wall in Sections 503.1 and 706.1 is predicated on the determination of the maximum allowable height and area calculations under Chapter 5. Using these sections of Code to control other building features or elements such as means of egress, building systems or building utilities is not intended or implied by these sections of the Code. However, by inclusion of the first sentence in Section 706.1 some code officials have incorrectly interpreted that language to mean that the portions of the various elements and systems on each side of a fire wall must be completely self-contained. There are no requirements in the I Codes that mandate that the placement of fire walls to create a separate building such that its building features need to be separated from other like building features in adjacent buildings. The scope of Section 706 is to provide the technical requirements for the construction of a fire wall.
The added language in Section 503.1 along with the strikeout and added language in Section 706.1 will clarify application of these two sections.
G 130-15 Committee Action:
Approved as Submitted
Committee Reason: The proposal clearly separates the scoping of fire walls from the design requirements for fire walls. Section 706.1 is the location of the standards for fire walls and is similar other provisions in Chapter 7 which are the 'cook books' for each type of wall and horizontal assemblies. The committee hopes that this will reduce requests for duplication of other systems such as sprinkler systems, electrical systems, etc, in each portion of a structure separated by fire walls. The new text in 503.1 clearly states why fire walls are needed for addressing height and area limitations as well as type of construction.