• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Does a storage room in R-2 occupancy require a separation?

error404

Bronze Member
Joined
Jun 10, 2013
Messages
49
Location
United States
IBC 03 & 09 NFPA

They are new apartment units; each with a storage room. Storage room will be accessed from the open breezeway (that connects all the units).

One of the storage room will be 93 sq.ft. (the rest will be less than 50 sq.ft.).

Building will be sprinkled

thanks in Advance!
 
I would say no separation required based on 2003 IBC Table 302.1.1 Incidental Use Areas, storage rooms over 100 sq. ft. require 1 hr or sprinklered. FYI they took parking and storage areas out of the 2009 IBC incidental use area table.
 