• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Does an existing warehouse under 12,000 sq ft require sprinklers?

mercyheartband@gmail

Registered User
Joined
Feb 26, 2024
Messages
1
Location
North Carolina
Does an existing building that is under 12,000 sq ft require an automatic fire sprinkler system? 24 ft ceiling height. Standard products being stored. No building alterations, just a new tenant. Oklahoma City area
 
Standard products being stored

Additional information will need to be provided.

903.2.9 If Group S-1 fire area exceeds > 12,000 sq ft. Verify all types of storage in that section tire storage, furniture etc.

See section 311 for types of storage classification: Group S-1 Moderate-hazards or Group S-2 Low-hazard storage
 
New occupant, same use, code compliant before.........move along. We issue a new C.O. for sales tax collection purposes and documentation.
 
[A] CHANGE OF OCCUPANCY. Any of the following shall be considered as a change of occupancy where the current International Building Code requires a greater degree of safety, accessibility, structural strength, fire protection, means of egress, ventilation or sanitation than is existing in the current building or structure:
  1. Any change in the occupancy classification of a building or structure.
  2. Any change in the purpose of, or a change in the level of activity within, a building or structure.
  3. A change of use.
 
Would you be able to use the IEBC if there are no alterations?

For jurisdictions that have adopted it, the IEBC is the starting point for anything pertaining to existing buildings: repairs, alterations, changes of use, and additions. You have to look at the applicable chapters, depending on the parameters of the project.
 