• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Does stair to mechanical room still need a landing?

ccollings

SAWHORSE
Joined
Sep 4, 2020
Messages
103
Location
Cleveland
I have a second floor mechanical space. the floor to floor height is 14'-8".
does the access stair need a landing because the vertical rise is greater than 12' per IBC 1011.8?
my interpretation is yes but a coworker thinks it doesn't because the stair is not serving an occupied space per IBC 1011.1
the mechanical room is approx. 2000 sf. the space is required to have 2 exits and the second exit is a ladder to the roof (IBC 1006.2.2.2)
Thank you for your thoughts.
 
the mechanical room is approx. 2000 sf. the space is required to have 2 exits and the second exit is a ladder to the roof (IBC 1006.2.2.2)

This says it all, Yes for the landing, its 2,000 sqft with equipment in it, not 150 sqft with just one pc of equipment.

The simple fact its required to have 2 moes says it all....
 
2,000 S.F. of anything (including a space for mechanical equipment) should require all of the normal safety provisions. That is a big space. Hmmm.
 