• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Does the IBC require stair rails?

Matt M

REGISTERED
Joined
Feb 6, 2019
Messages
3
Location
Great Falls, MT
I know OSHA regulations require stair rails around unprotected sides and edges of stairways during construction. Does anyone know if it's required for non-OSHA projects?
 
I believe this gives the AHJ the tools needed to require guards and barriers on construction sites that may not be under OSHA regulations. We have used this section to require the stairs to be installed in lieu of using ladders between floors.

[F] 3310.2 Maintenance of means of egress.
Means of egress and required accessible means of egress shall be maintained at all times during construction, demolition, remodeling or alterations and additions to any building.

Exception: Existing means of egress need not be maintained where approved temporary means of egress systems and facilities are provided.
 
Thanks for the response. I guess my question is this: does the general contractor have a responsibility to put a temporary guardrail or stair rail around an open stairwell during a remodel? Osha (29 C.F.R. § 1926.1052(c)) makes it pretty clear that you can't just leave the stairwell open because an employee could fall down the stairwell by accident. Even if it's a smart thing to do, I'm not sure if it's required under IBC.
 
Does your State/jurisdiction adopt Chapter 33 of the IBC? If so, check out Table 3306.1 and subsequent section 3306.4. Note that the requirements are for protection of pedestrians, not for on-site construction personnel.

However, if this is interior to the job and not used by the public, it is typically only governed by OSHA or other state safety board.
 
[F] 3310.2 Maintenance of means of egress. Required
means of egress shall be maintained at all times during construction,
demolition, remodeling or alterations and additions
to any building.
Exception: Existing means of egress need not be maintained
where approved temporary means of egress systems
and facilities are provided.
 
Is there a required "Means of Egress" during construction?
I don't think so, it is a construction safety issue. Not in the purview of a building department.
Methods and procedures are not listed,,,,
 
Is there a required "Means of Egress" during construction?
I don't think so, it is a construction safety issue. Not in the purview of a building department.
Methods and procedures are not listed,,,,

Depends...
3302.1 Alterations, repairs and additions. Required exits,
existing structural elements, fire protection devices and sanitary
safeguards shall be maintained at all times during alterations,
repairs or additions to any building or structure.
Exceptions:
1. Where such required elements or devices are being
altered or repaired, adequate substitute provisions
shall be made.
2. Maintenance of such elements and devices is not
required when the existing building is not occupied.
 
So there is a dangerous condition at a construction site and apparently someone needs convincing that it should be corrected. I explain the danger and then refuse to get anywhere near it. If I can’t get near it, I can’t inspect whatever needs inspecting. The job usually stops proceeding if I’m not inspecting. They have always been reasonable.

For the naysayers....please note that I did not mention OSHA.
 
The building code is interested in protecting the public and doesn't really address construction worker safety.

Most states' Department of Labor have a state specific version of OSHA that would definitely include this and would definitely apply to any construction contractor. I believe some states use the federal OSHA rules and I think you can look those up on the OHSA web site. But the first place to look is your state's Department of Labor website and search for Construction Safety.
 
1926.1052(c) Stairrails and handrails
The following requirements apply to all stairways as indicated:
1926.1052(c)(1)
Stairways having four or more risers or rising more than 30 inches (76 cm), whichever is less, shall be equipped with:
1926.1052(c)(1)(i)
At least one handrail; and
1926.1052(c)(1)(ii)
One stairrail system along each unprotected side or edge.
Note: When the top edge of a stairrail system also serves as a handrail, paragraph (c)(7) of this section applies.
1926.1052(c)(2)
Winding and spiral stairways shall be equipped with a handrail offset sufficiently to prevent walking on those portions of the stairways where the tread width is less than 6 inches (15 cm).
1926.1052(c)(3) The height of stairrails shall be as follows:
1926.1052(c)(3)(i) Stairrails installed after March 15, 1991, shall be not less than 36 inches (91.5 cm) from the upper surface of the stairrail system to the surface of the tread, in line with the face of the riser at the forward edge of the tread.
 
1926.1052(c) Stairrails and handrails
The following requirements apply to all stairways as indicated:
1926.1052(c)(1)
Stairways having four or more risers or rising more than 30 inches (76 cm), whichever is less, shall be equipped with:
1926.1052(c)(1)(i)
At least one handrail; and
1926.1052(c)(1)(ii)
One stairrail system along each unprotected side or edge.
Note: When the top edge of a stairrail system also serves as a handrail, paragraph (c)(7) of this section applies.
1926.1052(c)(2)
Winding and spiral stairways shall be equipped with a handrail offset sufficiently to prevent walking on those portions of the stairways where the tread width is less than 6 inches (15 cm).
1926.1052(c)(3) The height of stairrails shall be as follows:
1926.1052(c)(3)(i)
Stairrails installed after March 15, 1991, shall be not less than 36 inches (91.5 cm) from the upper surface of the stairrail system to the surface of the tread, in line with the face of the riser at the forward edge of the tread.

So I was looking at this, but wouldn't it only apply if the job was an OSHA job?
 
If You do have OSHA where you live and work....ask yourself if you have the authority to enforce OSHA regulations.

Some will find that their authority stops at the end of their nose. If that’s true for you...be bold....do what needs to be done. Don’t care about getting chewed out....it happens.
 
Agreed, however the OP appears to be from Montana, hence the reference to the Federal OSHA Standards (which MT follows) under 1926.1052(c)
Correct federal OSHA for private sector employees.
Public sector employees fall under Montana's recently adopted state plan.

Comparison: State vs. Federal
• Rules. Montana is not a "state plan" state; that is, it does not have a federally approved occupational safety and health regulatory program. Therefore, the federal OSHA Act governs occupational safety and health in the private sector (private businesses and nonprofit organizations) workplace in Montana. For information on the federal requirements, see the national sections HAZARD COMMUNICATION STANDARD, MATERIAL SAFETY DATA SHEET, OSHA, and TRAINING.

Public sector (local and state government offices and operations) employers in Montana are subject to state workplace safety and health requirements. State standards mirror the OSHA Act requirements.
 
Back
Top