Hi Simonsays –
IMO the answer is no. The IFC does not dictate the type of system, e.g., addressable or conventional. Section 907.3.1 does not state anything about addressable nor is it implicit in the requirements of that section that would lead me to that conclusion. I feel that it would be “reading into the code” if someone feels they are required to be addressable. Another thing to consider is that NFPA 72 does not require addressable systems/devices either and manufacturers still make conventional panels and devices, as well. There are some jurisdictions that have requirements for addressable systems that I have run across but not the model code. Although not required to be addressable, they must be connected to the fire alarm system (assuming it is a required system) so the system installed would drive how you are likely to monitor it. Hope this helps.