California Building Code 2022
Type V-B non sprinklered.
B occupancy
We are working on a project that had an electrical room planted on the front of the building sometime in the 70's. The electrical room was constructed under the existing flat roof overhang. The overhang and the electrical room long wall are on the property line. This is a front property line along the public sidewalk and street.
The inspector is suggesting that this electrical room needs to be 1-hour fire rated. There is no electrical reason for any rating. I was concerned about the distance to the property line as that is essentially zero. But from what I am seeing in Chapter 7 is that the Fire Separation Distance along this property line is actually to the center line of the street. From table 705.5 between 5-10 feet separation would require 1 hour exterior wall rating. Any separation above 10' would not require a rated exterior wall.
Am I missing something? We are greater than 10' from the interior property line to the adjacent left side wall more than 30' to the front wall if the FSD is measured to the CL of the street. snip below. That is the building switch gear inside the room.
Thank you, John

Type V-B non sprinklered.
B occupancy
We are working on a project that had an electrical room planted on the front of the building sometime in the 70's. The electrical room was constructed under the existing flat roof overhang. The overhang and the electrical room long wall are on the property line. This is a front property line along the public sidewalk and street.
The inspector is suggesting that this electrical room needs to be 1-hour fire rated. There is no electrical reason for any rating. I was concerned about the distance to the property line as that is essentially zero. But from what I am seeing in Chapter 7 is that the Fire Separation Distance along this property line is actually to the center line of the street. From table 705.5 between 5-10 feet separation would require 1 hour exterior wall rating. Any separation above 10' would not require a rated exterior wall.
Am I missing something? We are greater than 10' from the interior property line to the adjacent left side wall more than 30' to the front wall if the FSD is measured to the CL of the street. snip below. That is the building switch gear inside the room.
Thank you, John