Is a fusible link hold open closure allowed for door openings in a 2-hour fire barrier utilized to limit a fire area to less than 12,000 sq ft?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Item 6 deals with Fire Walls. I thought the OP asked about fire barrier walls.High Desert said:I think they have to be activated by smoke detectors (2009 IBC Section 715.4.8.3 Item #6).
That is for doors in a Fire Wall the OP stated Fire Barrier. I do not find a prohibition to a fusible link in the I-CodesHigh Desert said:I think they have to be activated by smoke detectors (2009 IBC Section 715.4.8.3 Item #6).
Sorry, read the OP too quickly. NFPA 80 will give specifics.Coug Dad said:Item 6 deals with Fire Walls. I thought the OP asked about fire barrier walls.