Why was this failed?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Plastic bushings for securing NM were properly installed.Fortner said:I don't see any box connectors for the NM. Was the metallic box bonded? I believe you have to protect that doorbell transformer from damage also. Why is a GFI receptacle in the attic?
Article 450 does not apply to Class 2 and 3 transformers.Fortner said:450.21 (A)
There is no mixing of voltages in the same enclosure in this example.georgia plans exam said:Would it have to do with the mixing of voltage ratings in the same enclosure???GPE
BINGO!!raider1 said:The transformer would be marked "Not for installation in an attic" so 110.3(B) would be the applicable code section to fail this installation.Chris
The Class 2 conductors are not located in the same box with the power conductors.vegas paul said:725.136 (A)