This is a surprise to me, I was sure it made it into the codes, maybe something given up to get sprinkler approval? What about R327.5.2?
[QUOTE='2013 CRC]R327.5.2 Roof coverings. Where the roof profile allows a space between the roof covering and roof decking, the spaces shall be constructed to prevent the intrusion of flames and embers, be firestopped with approved materials or have one layer of minimum 72 pound (32.4 kg) mineral-surfaced nonperforated cap sheet complying with ASTM D 3909 installed over the combustible decking.
[/QUOTE]I know that's designed for the surface of roofs but when you have a roof over a roof wouldn't that apply?
I think it's R302.12 Draftstopping.
[QUOTE='2013 CRC]
R302.12 Draftstopping. In combustible construction where there is usable space both above and below the concealedspace of a floor/ceiling assembly, draftstops shall be installed so that the area of the concealed space does not exceed 1,000 square feet (92.9 m2). Draftstopping shall divide the concealed space into approximately equal areas. Where the assembly is enclosed by a floor membrane above and a ceiling membrane below, draftstopping shall be provided in floor/ceiling assemblies under the following circumstances:
....1. Ceiling is suspended under the floor framing.
....2. Floor framing is constructed of truss-type open-web or perforated members.
[/QUOTE]