Double-swing Door Maneuvering Clearances

fj80

Sawhorse
Joined
Jan 18, 2016
Messages
230
Location
Virginia
What are the ADA requirements for maneuvering clearances for a double-swing door?
I don't see it in Chapter 4.

And can a door swing into the maneuvering clearance for another door?
 
2010 ADASAD 404.2.2 Double-Leaf Doors and Gates. At least one of the active leaves of doorways with two leaves shall comply with 404.2.3 and 404.2.4.

One, not both.
 
Why should they be outlawed? They don't latch, and you just push them to go either way. They're most commonly on building entrances.
 
Great reasoning
We need to rewrite the code based on likes and dislikes
Does everyone get a vote or just you?
Hold on here it comes.......
 
Great reasoning
We need to rewrite the code based on likes and dislikes
Does everyone get a vote or just you?
Hold on here it comes.......


As long as they vote my way.

Besides deaths, codes are changed because one person wants a change, and submits a request.
 
Apparently some think not allowed in some circumstances, even though black and white does not say that;;;;


“ I recently received a question regarding a location where a double-acting door would be serving as part of the means of egress for more than 50 people in both directions. Imagine a corridor with an exit at each end and a double-acting door in the middle, and 50 occupants on each side of the building. Would this be permissible?

From a common-sense standpoint the answer would be “no,” because 50 people pushing on each side of a double-acting door would be going nowhere. Since the model codes don’t specifically address double-acting doors, I asked the ICC for a staff opinion. The ICC staff member’s response was that a single double-acting door would not be acceptable in this case – that two separate doors or a double-egress pair would be required.”””

http://idighardware.com/2016/06/double-acting-doors/
 
Icbo 1997


double-acting doors - not acceptable as exit doors if the occupant load served by the door is over 100, if the door is part of a fire or smoke- and draft-control assembly, or if panic hardware is required; double-acting doors require view panels of at least
200 square inches



The good old days
 
From a common-sense standpoint the answer would be “no,” because 50 people pushing on each side of a double-acting door would be going nowhere.

I have to say, from a common-sense standpoint, having a single-acting door with 49 people on the pull side won't be too much of an improvement. The push-side people will get the door open 3', then they will be up against 49 very determined bodies.
 
  • Like
Reactions: cda
Icbo 1997
double-acting doors - not acceptable as exit doors if the occupant load served by the door is over 100, if the door is part of a fire or smoke- and draft-control assembly, or if panic hardware is required; double-acting doors require view panels of at least
200 square inches
The good old days
what section?
 
what section?



Maybe

Swing and Opening Force (1003.3.1.5)
· exit doors serving 10 or more occupants - pivoted, balanced,
or side-hinged swinging type
· shall swing in the direction of exit travel where the area served
has an occupant load of 50 or more; Group H exit and exit-access doors must swing in the direction of exit travel regardless of occupant load (1007.4.4); Group I required exterior exit doors shall open in the direction of exit travel regardless of occupant load (1007.5.5); refrigeration machinery rooms - doors shall swing in the direction of exit travel, regardless of the occupant load served, and shall be tight-fitting and self-closing (1007.7.2.3)
· opening force of 30 pounds applied to the latch side shall swing door to the fully open position (references to more information included, and exceptions for detention, dwelling units, and special doors)





Has to be right;;;


http://www.institutionallocksmiths.org/store/IR Fire Life and Safety Code Book.pdf
 
Hospital corridors often have pairs of 4-0's swinging in opposite directions in rated frames to allow gurneys to bypass.
 
Same as any other door, you are only using one side at a time...And Yes...
Aren't those doors meant to open at the same time if you run into them in the middle with a cart or say, a wheelchair? I'm just trying to decide if a pair of 2's would be code compliant. Maybe it comes down to the force required to open both at the same time? Any advice is welcome.
 
Aren't those doors meant to open at the same time if you run into them in the middle with a cart or say, a wheelchair? I'm just trying to decide if a pair of 2's would be code compliant. Maybe it comes down to the force required to open both at the same time? Any advice is welcome.
The original post in 2017 was not talking about a pair of doors. I was talking about a single door that swings in either/both directions, like you may often see at a commercial kitchen. For that kind of door, the only accessible clearances required are push side clearances.

What you are describing seems to be a pair of 2' wide doors that collectively provide a 4' wide opening when both are opened at once.
2010 ADAS 404.2.2 calls this a "double-leaf door", and requires at least one leaf to provide 32" clear width per 403.2.3.
 