1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Drain Holes for PVC Conduit

Discussion in 'Electrical Codes' started by jar546, Sep 13, 2019.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    If a 2" schedule 80 PVC conduit ran vertically down the outside of a building then stopped at an LB which then took it inside and the contractor wanted to drill a weep hole in the bottom of the LB (before they pulled wire of course) in order to facilitate drainage of water from the conduit body, what is the largest size hole the EC would be allowed to drill in the bottom of the LB PVC conduit body?
     
  2. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    7,385
    Likes Received:
    855
    How is water getting into the conduit in the first place? Not sure what you are asking
     
  3. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    Exterior conduit is inherently wet as it is not waterproof. Condensation can add to this issue. There are NEC codes that address this issue.
     
  4. chris kennedy

    chris kennedy Sawhorse

    Joined:
    Oct 24, 2009
    Messages:
    1,441
    Likes Received:
    156
    No holes allowed.
     
  5. TheCommish

    TheCommish Sawhorse

    Joined:
    Sep 27, 2011
    Messages:
    825
    Likes Received:
    119
  6. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    Holes Allowed
     
  7. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    314.15 Damp or Wet Locations. In damp or wet locations,
    boxes, conduit bodies, outlet box hoods, and fittings shall be
    placed or equipped so as to prevent moisture from entering or
    accumulating within the box, conduit body, or fitting. Boxes,
    conduit bodies, outlet box hoods, and fittings installed in wet
    locations shall be listed for use in wet locations. Approved
    drainage openings not smaller than 3 mm (1∕8 in.) and not
    larger than 6 mm (1∕4 in.) in diameter shall be permitted to be
    installed in the field in boxes or conduit bodies listed for use in
    damp or wet locations.
    For installation of listed drain fittings,
    larger openings are permitted to be installed in the field in
    accordance with manufacturer’s instructions.
     
  8. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    And then there is this. Remember 2017 required a minimum diameter hole in addition to the maximum size hole, unless, of course, you are using a listing fitting for this purpose.
    Screen Shot 2019-09-15 at 10.41.12.png
     
  9. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    This has been common practice for years. Here is an example from PPL Electric Utilities that require drainage holes to be drilled into the vertical conduit and sweep for underground installations when installing the conduit for their service laterals.

    Screen Shot 2019-09-15 at 10.44.47.png Screen Shot 2019-09-15 at 10.44.32.png
     
  10. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    There are often times in areas that are not flat, such as Florida, where a pad mounted utility transformer or hand-hole are located at a level much higher than the home and meter base. I have personally witnessed water pouring out of a meter base when a hand hole became full of water along a roadway and was draining into the meter base.
     
  11. chris kennedy

    chris kennedy Sawhorse

    Joined:
    Oct 24, 2009
    Messages:
    1,441
    Likes Received:
    156
    If you ask a question specifying a code cycle might be a good idea there genius.
     
    jar546 likes this.
  12. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    It's in the 2014, the current code for Florida and 42 other states which have the 2014 or 2017 (most have the 2017). Only one state has the 2011 and three states are still under the 2008. Yes, I should have specified the code cycle.

    Then there is Arizona, Mississippi and Missouri which have zero NEC adoption although some cities may have some codes to follow.
     
  13. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    You need to stop looking in the 2011 which hasn't been relevant in Florida since Jan 1, 2018. We have 1 year and 3-1/2 months left for the 2014 then on to the NEC 2017.
     
  14. chris kennedy

    chris kennedy Sawhorse

    Joined:
    Oct 24, 2009
    Messages:
    1,441
    Likes Received:
    156
    I like the 2011
    It has tabs!
     
  15. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    You can put them on any version ya know. Joe will buy them.
     