Drain pan under attic air handler

TheCommish

SAWHORSE
Joined
Sep 27, 2011
Messages
2,147
Location
Charlton Ma
Air handler in attic, correct drain pan installed. do the drain have to be to daylight or can the pan be used as storage with high level switch? Seem to be stated as an or list. Even though gravity drain would be the better way to go.

1749908359209.png

M1411.3.1 Auxiliary and Secondary Drain Systems​


In addition to the requirements of Section M1411.3, a secondary drain or auxiliary drain pan shall be required for each cooling or evaporator coil where damage to any building components will occur as a result of overflow from the equipment drain pan or stoppage in the condensate drain piping. Such piping shall maintain a minimum horizontal slope in the direction of discharge of not less than 1/8 unit vertical in 12 units horizontal (1-percent slope). Drain piping shall be not less than 3/4-inch (19 mm) nominal pipe size. One of the following methods shall be used:
  1. A separate overflow drain line shall be connected to the drain pan installed with the equipment. This overflow drain shall discharge to a conspicuous point of disposal to alert occupants in the event of a stoppage of the primary drain. The overflow drain line shall connect to the drain pan at a higher level than the primary drain connection.
  2. An auxiliary drain pan without a separate drain line shall be installed under the coils on which condensation will occur. This pan shall be equipped with a water level detection device conforming to UL 508 that will shut off the equipment served prior to overflow of the pan. The pan shall be equipped with a fitting to allow for drainage. The auxiliary drain pan shall be constructed in accordance with Item 1 of this section.
  3. A water-level detection device conforming to UL 508 shall be installed that will shut off the equipment served in the event that the primary drain is blocked. The device shall be installed in the primary drain line, the overflow drain line or the equipment-supplied drain pan, located at a point higher than the primary drain line connection and below the overflow rim of such pan.
 
You don’t need a drain to daylight if you're using a properly installed UL 508 water-level detection device. The code gives three options, and any one of them is acceptable. A gravity drain is the most reliable method, but it’s not required if you have a compliant high-level shutoff switch in the pan or drain line.
 