Porch with roof (ply, ice and water, architectural shingles) and ceiling. LED down lights in ceiling. NM-B or UF?
Thanks.
Thanks.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
I take that to refer to wiring exposed within the user portion of the roofed open porch, and so possibly directly exposed to moisture from the side. Whereas I understand the OP to be about wiring in the porch's "attic," which would not be so exposed, and hence would be a dry location. Like any other attic.Location, Damp. . . . roofed open porches
NEC 410.10(D) is pretty clear about when a luminaire near a shower needs to be damp or wet rated. Outside the (projected) footprint of the shower only requires a dry location rating.Every bathroom with a shower could be damp.
Unless the roof above the soffit leaks, the wiring above the soffit would be in a dry location. Whether the luminaire exposed through the soffit needs to be damp location rated depends on your interpretation, but if close to the roof edge, using a damp location luminaire seems like a good idea.Now it makes me wonder if lights recessed in a soffit and the wiring is dry or damp?
It’s dry or it’s wet. There is no damp.but if close to the roof edge
If your referring to the location of a recessed luminaire in the soffit of a roof overhang, I certainly don't agree.It’s dry or it’s wet. There is no damp.
My understanding is that the only product available these days that meets the NM-C standards is UF.You can still use NM cable, it just has to be NM-C.
Indeed. Moisture is liquid water, not humidity or water vapor. How much liquid water will the attic see? Should be none.Location, Damp. (Damp Location)
Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. (CMP-1)
A moderate degree of moisture would be water vapor, which is water in a gaseous state, and when it reaches its dew point, it will have a change of state and condense into water due to a temperature change. No water should be in the attic to saturate the wiring, but the fixture being outside the envelope and exposed to high humidity will condensate into water, and the wiring in the fixture will become wet. And the cycle will continueMy understanding is that the only product available these days that meets the NM-C standards is UF.
Indeed. Moisture is liquid water, not humidity or water vapor. How much liquid water will the attic see? Should be none.
Cheers, Wayne
So you don't allow NM-B in an attic, because it's not in the thermal envelope?100% Damp Location. Concerning the fact that it is inside an "attic" space. It is outside the thermal envelope, and often, there is no access to these areas. We all know the implications of hot, humid summers and the dampness of the winter without sunlight. You can still use NM cable, it just has to be NM-C.
Location, Damp. (Damp Location)
Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. (CMP-1)
Informational Note:
Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some cold-storage warehouses.
While the term "moisture" is sometimes used to refer to water vapor (e.g. "moisture in the air"), in this context it is only referring to liquid water.A moderate degree of moisture would be water vapor
Never said that. I used it descriptively, and you ran with that part of the sentence. I should know better.So you don't allow NM-B in an attic, because it's not in the thermal envelope?
Well, explain. You seemed to say the attic of a porch was damp and now am not sure about the attic if a houseNever said that. I used it descriptively, and you ran with that part of the sentence. I should know better.
See post #20Well, explain. You seemed to say the attic of a porch was damp and now am not sure about the attic if a house
I also don't know if it's different where you are versus where I am. Florida seems like a humid place. Here on the border with Canada, it's usually very dry, except out in the rain.
Since when is an informational note code text.it’s in the code text.
You are misinterpreting the definitions.The NEC makes this distinction clear
Actually it says "partially protected locations under . . . roofed open porches." If your porch has a ceiling, the area above it is fully protected, and not a damp location. Likewise, I'd say a location exposed on (the bottom face of) the ceiling sufficiently far from any of the roof edges is fully protected. While it is at least plausible that a location on the ceiling right next to the roof edge is only partially protected.A roofed open porch is listed in the Informational Note as a damp location.
A porch has a roof, and if it has a ceiling, the space between the roof and ceiling meets all the conditions of an attic you mention in the second paragraph. You have not demonstrated a material difference between such a vented, enclosed space with conditioned space under the ceiling (the attic of the the house) or unconditioned open space under the ceiling (the attic of an open porch).The reason is simple: a vented porch ceiling is continuously exchanging air with the exterior environment. In South Florida or anywhere on the East Coast in summer, that means constant humidity, condensation potential, and occasional wind-driven rain. That is not the same as an attic.
An attic is an enclosed cavity that, while vented, is separated from direct exterior exposure by roof decking and other construction. That’s why the NEC allows NM-B in attics but not in porch ceilings.