Unfortunately 1502.4.2 for residential dryers instead of enhancing the article with requirements, it references 1601.4.1 for other ducts.fatboy said:I think there is mixing and mis-matching of systems. Are we talking about a clothes dryer exhaust, or a duct system. Different chapters, different requirements..............
I would be concerned that screws/rivets will catch lint and create a hairball the size of a cat. How will you know how far the screws/rivets project into the duct? If it is put together correctly, there should not be a way for it to fall apart.Coder said:Thinking that a couple pop rivets or tiny sheet metal screws at each connection will be what I am requiring from here on out. Worried about dryer exhausts in concealed spaces falling apart with no one knowing.
Consider most of the time is spent on the main level and will be forced to make multiple trips to the upper level for the washing and drying cycles especially if doing several loads.JBI said:MASSDRIVER, LOL. The trend of laundry rooms upstairs surprised me the first time someone proposed it. The prospective homeowner (an old friend) pointed out that 90% or more of the laundry was generated upstairs - clothing, bedding - hence it was a convenience as opposed to schlepping the laundry down and then up stairs again. Actually makes sense and I've considered moving mine to the top floor.
Coder said:2015 International Mechanical Code (IMC) Section 504.6.2 was revised to allow domestic clothes dryer exhaust duct sections to be joined with screws or similar fasteners which do not protrude more than 1/8" into the inside of the duct. This section now coincides with the requirements in the IRC.
This is what I am thinking I can hang my hat on. Will be adopting the 2015 in a couple years anyways.
the screw that sticks an inch into the duct.So then at each such inspection one must ask that a screw be removed. Then the victim will be informed that they have used the wrong screw. Debate will commence. Ridicule will ensue. Screw that.I can hang my hat on
...or, don't screw it and use tape.ICE said:Debate will commence. Ridicule will ensue. Screw that.
How about metal hose clamps? I'm not fond of the screw method either ICE, but if it is allowed in the 2015 code then I guess it needs to be addressed (or amended out).Francis Vineyard said:Necessity being the mother of invention; could be a market for dryer duct seamless locking clips or buttons.
When it gets here it's gone. I reckon a zip tie and tape will suffice.Coder said:How about metal hose clamps? I'm not fond of the screw method either ICE, but if it is allowed in the 2015 code then I guess it needs to be addressed (or amended out).
I would tend to agree that the sections are different, and it would be rare for me to write that correction if things appear to be properly supported. If there is not strain on the joints, I personally have bigger fish to fry.Now I contest that a dryer vent system is not a duct system, and that that rule does not supersede IMC 504.8.2
Definition for "mechanically fastened"? Only screws or rivets, or crimping, banding, other?shall be mechanically
fastened