Our office faced an interesting question recently. The issue - as I understand it - is that a clothes dryer has been vented through (according to the client, haven't seen it myself yet) 25' of pipe, with five turns. That seems mighty problematic to me. (Searching Ontario building commission/BC code interps/BC Code Commission rulings gave me nada.)
NBC 9.32.1.3 states that dryers shall be vented "directly" to the exterior, with no definition of "directly."
Table 9.32.3.11-A is the duct airflow/diameter/length matrix. I feel it applies - anyone disagree? If so, why?
Presuming 9.32.3.11-A applies, a residential dryer generates about 150-200 CFM, or about 82-94 L/S.
It's about here where I get lost, because I'm not sure how to determine a dryer's static air pressure. My gut at the moment would be to determine the dryer manufacturer/model, and work from there. I'm presuming it's 'murrican with fan pressure in column-inches that I can convert to Pascals and work things through from there. Based on some interweb stalking, it seems the static pressure of a dryer is usually no lower than 75 Pa.
Presuming a 4" (100mm) duct and a 75 Pa fan pressure (as a start) I'm calculating a 1-3m duct limit. This seems remarkably small, so I assume I'm off the deep end.
Help?
Our office faced an interesting question recently. The issue - as I understand it - is that a clothes dryer has been vented through (according to the client, haven't seen it myself yet) 25' of pipe, with five turns. That seems mighty problematic to me. (Searching Ontario building commission/BC code interps/BC Code Commission rulings gave me nada.)
NBC 9.32.1.3 states that dryers shall be vented "directly" to the exterior, with no definition of "directly."
Table 9.32.3.11-A is the duct airflow/diameter/length matrix. I feel it applies - anyone disagree? If so, why?
Presuming 9.32.3.11-A applies, a residential dryer generates about 150-200 CFM, or about 82-94 L/S.
It's about here where I get lost, because I'm not sure how to determine a dryer's static air pressure. My gut at the moment would be to determine the dryer manufacturer/model, and work from there. I'm presuming it's 'murrican with fan pressure in column-inches that I can convert to Pascals and work things through from there. Based on some interweb stalking, it seems the static pressure of a dryer is usually no lower than 75 Pa.
Presuming a 4" (100mm) duct and a 75 Pa fan pressure (as a start) I'm calculating a 1-3m duct limit. This seems remarkably small, so I assume I'm off the deep end.
Help?