1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Drywall Screws in Joist Hangars

Discussion in 'Residential Structural Codes' started by jar546, Aug 15, 2019.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,071
    Likes Received:
    526
    Not only are there unused holes but.............
    Insert code violation number here:

    IMG_1669.jpg
     
  2. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,587
    Likes Received:
    901
    How many do you want?

    R104.9 Approved materials and equipment. Materials,
    equipment and devices approved by the building official shall
    be constructed and installed in accordance with such
    approval

    R106.1.2 Manufacturer’s installation instructions.
    Manufacturer’s installation instructions, as required by
    this code, shall be available on the job site at the time of
    inspection.

    R502.6.2 Joist framing. Joists framing into the side of a
    wood girder shall be supported by approved framing
    anchors or on ledger strips not less than nominal 2 inches
    by 2 inches (51 mm by 51 mm).
     
  3. e hilton

    e hilton Bronze Member

    Joined:
    Jul 2, 2014
    Messages:
    441
    Likes Received:
    101
    Looks like the hanger is fastened to the web of an i-joist. Don’t think the mfgr allows that.
     
  4. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,679
    Likes Received:
    447
    Looks like LVL to me.
     
  5. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    3,012
    Likes Received:
    396
    R106.1.2 in regards to the SST hanger, drywall screws would not be permitted but SST screws would. So the hanger would not be installed correctly per manufactures instructions. I believe the correct hanger is being used for a 1.5 width framing lumber unless the plans state otherwise. GP and TJI allow both USP and Simpson hanger usage with this type LVL beam.
     
  6. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,783
    Likes Received:
    358
    Simpson loves these for their road show on "what not to do" with their hangers.
     
  7. my250r11

    my250r11 Sawhorse

    Joined:
    Feb 16, 2015
    Messages:
    557
    Likes Received:
    157
    Those don't look to be the correct Simpson hard nails for the hanger, appear to be 2 different types of nails as well.
     
  8. e hilton

    e hilton Bronze Member

    Joined:
    Jul 2, 2014
    Messages:
    441
    Likes Received:
    101
    I was interpreting the plywood where the caption is ... to be the flange of the joist. You could be right.
     