Duct chase in mixed use 2 story building. Can I call it a "two story opening"

Fast_Edd1e

REGISTERED
Joined
Jun 30, 2021
Messages
36
Location
Michigan
I have a non-separated mixed use building. Fully fire suppressed. Wood framed. 2015 michigan building code. One portion of the building has 5 apartments above a business space. Apartments only need to be 1/2 hour rated since we are fully fire suppressed. Walls are 5/8 each side. Doors are rated. Ceiling is 5/8 on rc-1. Floor is 1.5" gypcrete.

Does the gypcrete compartmentalize the apartments or would the whole lower level need a 1 hour floor/ceiling assembly?

This brings me to the main question. We have a duct chase going from roof to lower level. Framers did not give enough space with their joists. So we are trying to avoid calling this a Shaft since its a wood joist and cant penetrate a shaft. This chase we can provide an access to so its not concealed. And its not on a corridor. And complies with all other requirements of 712.1.9 Two Story Openings. But if we have the entire floor/ceiling assembly below as rated and not covered by just the 1.5" gypcrete in the apartments, we would be penetrating a rated assembly. Which throws us into a Shaft and required to be rated.

Otherwise, im assuming the only option is to encapsulate the wood joist running thru the shaft to protect it. Which is difficult but doable.
 
The gypcrete is more about sound than fire I believe.....
Access panels do not make it "not concealed"
Wood exposed in the "shaft"? Make sure you get sprinklers in it or have a specific exemption from NFPA 13...

Good Luck!
 
IMC 607.6.1 allows a duct to connect not more than two stories without a shaft if a fire damper is installed at the floorline.
Hmm. That might help avoid calling it a rated shaft enclosure and alleviate our issues if we seal the duct off at the floor with a damper.
 
Fire burns upward. The fire protection of floor/ceiling assemblies is provided by the ceiling. The gypcrete floor is typically only for sound. Without the ceiling (gyp board), joists burn, floor falls, and the gypcrete does nothing.
 
Fire burns upward. The fire protection of floor/ceiling assemblies is provided by the ceiling. The gypcrete floor is typically only for sound. Without the ceiling (gyp board), joists burn, floor falls, and the gypcrete does nothing.

Correct -- mostly. You are correct that fire/heat [mostly] burns up and it is the ceiling that is important in a rated floor-ceiling assembly, BUT ... it's rare to find a rated ceiling. What we usually find in the U.L. Design book (or, now, web site) and in the Gypsum Association Handbook is rated floor-ceiling assemblies. It's the assembly that is rated, and if you remove any part of the assembly -- it's no longer a rated assembly.
 
Correct -- mostly. You are correct that fire/heat [mostly] burns up and it is the ceiling that is important in a rated floor-ceiling assembly, BUT ... it's rare to find a rated ceiling. What we usually find in the U.L. Design book (or, now, web site) and in the Gypsum Association Handbook is rated floor-ceiling assemblies. It's the assembly that is rated, and if you remove any part of the assembly -- it's no longer a rated assembly.
Correct. I simplified it down for the OP who did not appear to understand the concept.
 
There are a few systems, such as Gypsum Association #FC 5406 - 5408, where the "Ceiling provides one hour fire resistance protection for framing, including trusses."
 