• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Ducts on roof

Nothing in the IRC for ducts that are out side the building envelope and not in an attic. Commercial addresses it

2018 IECC
C403.11.1 Duct and plenum insulation and sealing (Mandatory).
Supply and return air ducts and plenums shall be insulated with not less than R-6 insulation where located in unconditioned spaces and where located outside the building with not less than R-8 insulation in Climate Zones 1 through 4 and not less than R-12 insulation in Climate Zones 5 through 8. Where located within a building envelope assembly, the duct or plenum shall be separated from the building exterior or unconditioned or exempt spaces by not less than R-8 insulation in Climate Zones 1 through 4 and not less than R-12 insulation in Climate Zones 5 through 8.
 
1601.4.6 (2) Exterior duct systems shall be protected against the elements.
1103.3.1 Has insulation values - but only speaks to ducts in attics, ducts in other portion of the building and ducts completely within thermal envelope.

If the IRC doesn't cover a topic, reference IBC and its relevant section?
 