• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Egress: 2 Separate Rooms into 1

eyan50495

Registered User
Joined
May 18, 2020
Messages
71
Location
Locust Valley, NY
Hi, we currently have 2 small workout recreation rooms that require 1 means of egress. Both rooms which are adjacent to one another have doors into a rated corridor.

The client wants to add a door between these adjacent rooms for access between them. However, if we count both floor areas together, the 2 rooms would require 2 means of egress. The existing doors are right next to one another and would not meet the remoteness requirement.

Would adding the door b/t both rooms trigger them to be counted as a single large room?
 
Well. Seems like the 2740 should have two exits to begin with

I take it sprinkled building ??

The two existing doors are not 1/3 diagonal distance apart?!
 