Egress and multi-story apartments
manifold
Member
Denver, CO
2022 Denver Building Code (2021 IBC), R-2 Apartment building, Type III-B, sprinklered.
A client presented me with some SD drawings for a small apartment building with a single egress stair. This is allowed up to 3 stories. The apartments with their entry on the third floor have 2 floors within them, plus a roof top deck that are accessed by an internal stair. The upper floor and roof deck cover the full foot print of the unit so no mezzanine. Am I correct that the second level of the apartment would be a 4th story which would require a second exit? The occupied roof also has a 1200 SF "Recreation Area" that I would consider an assembly space with 80 occupants, which seems like it would also require a second exit.
Please let me know your thoughts.
Not really...it gets complicated...Do you get to the stair within 125'?
It mostly meets the 125’. There are a couple places on the roof deck that are over, but this can be fixed.
What are the details of the ‘complicated’ bits?
"Mostly meets" means "partially does not meet" the code. So = FAIL.
If the number is 125 feet, that's a hard maximum. 126 feet is a fail. 125'-6" is a fail. 125'-1" is a fail.
We had a saying when I was in the Army: "Close only counts in horseshoes and hand grenades."
Responding to a few items above:
There are a couple of locations at the private roof decks that are a foot or two more than 125' to an exit. These can be resolved by adjusting door, hall, stair locations to get the distance below 125', so not a major issue since fixable.
The upper floor of the units with their entry on the 3rd floor are 100% of the area of the floor below. So they would not be a mezzanine. I'm reading this as a 4th story that would require access to a second exit, mostly looking for confirmation of this.
my understanding of TABLE 1006.3.3(1) is that 125 feet is to the exterior, not the start of the exit. IE: they have to get OUT of the building in 125 feet, not INTO the stairwell within 125 feet. This makes sense to me because 125 feet is common path to two exits and you don't ever have access to two exits, thusly you have to get OUT within 125 feet. I've used this to permit 3 story apartment buildings, but they end up fairly small and the single stair ends up centrally located (usually) in order to get it done. I think for the building you are describing, the number of stories might be an issue, but regardless they can't get out within 125 feet. The design might be legal with "townhouse style" third floor units, that have a 4th floor plus roof deck (only one interior stair to the unit), but when they exit from the unit at the third floor level, they will need 2 stairs to get out.
That doesn't appear to be what the code language or the table says. How did you arrive at that conclusion?
I was interested to find that this section and this table don't exist in the 2021 IBC.
table TABLE 1006.2.1 in the 2021 IBC. Common Path. I'd be happy to be proven wrong - it'd give me more design options.
I do see that in the 2018 it references common path in two places, but in 2021 they called it "exit access travel distance" in the "stories with one exit" table for R2. Is that a clarification or a mistake?
I went down this road before. I was told it was errata which is noted in my books. I can't recall who confirmed this but I remember it was supposed to say EATD, not CPET, which made sense as CPET has no place in a table for single exits. It was revised in both the text and table in the 2021 IBC.
What if we have the stairs were in a two-hour rated enclosure. Similar to an egress exit into a separate "building" by going through a two-hour rated firewall.
So what?
What good is a stair in a 2-hour enclosure if the occupants on the fourth -- or sixth -- floor can't get to that one stair? That's why so many people died in the Grenfall Tower disaster -- they couldn't get to the exit stair.
It's an old saying that those who fail to learn from the mistakes of history are doomed to repeat them.
IMHO, a single 2 hour stairwell is essentially a horizontal exit - and code says that you can't have the only exit be a horizontal exit. We are currently working on a single exit 4 story building where the travel distance is too far, but what we did was put an exterior stair halfway down, so you are outside the building w/in the travel distance. Because of the weird topography on our site, this "halfway" exit is actually at grade.
A 2-hour stairwell is NOT a horizontal exit -- is is a vertical exit. The code is very clear on what constitutes a horizontal exit -- and it doesn't include stairs.
Note that the IBC definition of "Exit" clearly differentiates between interior and exterior stairs as exits, and horizontal exits.