Two exits are in the building - the ratings are not for fire walls so it is one building with two egress stairways at each end.
The stair shaft has a fire barrier to encapsulate the enclosed stair shaft and to partially enclose the open stair shaft. The balance of the separations are for the sleeping units (Dorm Rooms)
The only issue is the length of the dead end corridors are only allowed with a true NFPA 13 Fire Sprinkler system.....for 50 feet dead end corridors
if a 13R system is used, dead end corridors are only allowed to be 20 feet.
IBC Referenced here.